See the attached:
and from my General Notes:
HYDROVAC OPERATION
WORK TO BE UNDERTAKEN IN ACCORDANCE WITH ALL RELEVANT SAFETY CODES
PROVIDE SAFETY BARRIERS AS REQD
PROVIDE ‘WARNING/DANGER’ SIGNAGE AS REQ'D
ALL LOCATE DOCUMENTATION MUST BE CURRENT AND MUST BE WITH THE PERSON DOING THE EXCAVATION AT ALL TIMES
ASSUME ALL CABLES TO BE EXPOSED DURING THE HYDROVACING ARE ENERGIZED. SAFE WORK PRACTICES SHALL BE DEVELOPED BETWEEN THE OWNER THE CONTRACTOR TO ENSURE SAFETY WHILE WORKING AROUND LIVE CABLES. CONTRACTOR TO ENSURE ALL EQUIPMENT AND CABLES ARE NON-ENERGISED AT ALL TIMES INCLUDING PERIODS OF INACTIVITY
HYDROVAC TRUCK SHALL BE SUITABLY GROUNDED INTO THE EQUIPOTENTIAL ZONE. PROVIDE GROUNDING PADS FOR ALL WORKERS AS REQUIRED
CONTRACTOR TO ENSURE ALL EQUIPMENT AND CABLES ARE NON-ENERGISED AT ALL TIMES INCLUDING PERIODS OF INACTIVITY
HYDROVAC AS REQD TO EXPOSE ALL BURIED UTILITIES. TAKE CARE TO PREVENT OVER EXCAVATION
ABSOLUTELY NO MECHANICAL EXCAVATION WITHOUT PERMISSION
REMOVE EXCAVATED MATERIAL AND DISPOSE AS DIRECTED BY OWNER
HYDROVAC EQUIPMENT SHALL HAVE SUITABLY SIZED WATER RESERVOIR AND DISCHARGE TANK FOR THE WORK
WAND TIP SHALL BE EQUIPPED WITH A HIGH PRESSURE NOZZLE WITH A SINGLE JET OSCILLATING HEAD. DIRECTION OF WAND SHALL BE ACROSS CONDUCTORS AND NOT PARALLEL TO THEM. DIRECT HIGH PRESSURE NOZZLE IN A CIRCULAR PATTERN TO AVOID PROLONGED CONTACT WITH CONDUCTORS.
VACUUM NOZZLE SHALL HAVE A SOFT TIP (NEOPRENE OR EQUAL) TO PREVENT DAMAGE TO THE CONDUCTOR
WATER TEMPERATURE FOR HYDROVAC OPERATION SHALL NOT EXCEED 40%%CC. WATER PRESSURE SHALL NOT EXCEED 1500 PSIG
IF DAMAGE OCCURS TO CONDUCTOR, STOP WORK, AND PROCEED AS DIRECTED BY OWNER
Check with a local operator; this may not be suitable for some soils
Dik