Epoxy Injection in CMU

Status
Not open for further replies.

StructTaco

Structural
Jun 19, 2009
73
Is coring/testing necessary or advisable for a solid grouted 12" CMU wall. The crack is approximately 1/8" wide and 15' long.

Thanks, Dave
 
Replies continue below

Recommended for you

Do you know what caused the crack? What would you learn from coring? Was the reinforcement inspected?

BA
 
the crack was caused by a deteriorated sewer line, the foundations were wet and the corner of the building settled. I put crack monitors on and watched it for a year. The movement has stopped once the sewer line was fixed and the soils dried out. The soils were drilled on both sides of the wall and found to be fine a couple feet down.

The core would be used to determine if the epoxy bonded to the CMU and grout. If it broke at the epoxy/crack repair, no good. I found a spec on the SEAINT website, which discusses coring but says it may be waived in some situations, but I'm not sure which situations...
 
I think, given your information, that it depends on the importance, do you need to transfer stress through the repaired crack or is the repair for appearance only. If, as I imagine, the surfaces inside the crack are rough, there should be some mechanical interlock even if there is a lack of bond.

Michael.