Epoxy-coated steel bars shall comply with the requirements of ASTM A 775/A 775M, including written certifications for coating material and coated bars, sample of coating material, and 0.5 pounds of patching material.]
DELIVERY, STORAGE, AND HANDLING
A. Handling of Epoxy Coated Rebar:
1. Use padded or nonmetallic slings and padded straps to protect coated reinforcement from damage.
2. Handle bundled bars to prevent sagging that could damage the coating.
3. Do not drop or drag rebars.
4. Store on wooden cribbing.
5. Coated rebars subject to rejection by Engineer if rebar coating has been damaged.
2.04 FABRICATION
C. Ship rebars to jobsite with attached plastic or metal tags.
3. For epoxy coated rebars, use only plastic tags secured to rebars by nylon or plastic ties.
3. Rebar support:
b. Coated rebar:
1) Support coated rebars and fasten together to prevent displacement.
2) Use plastic or nylon ties to hold rebars rigidly in place.
3) Support rebars by use of plastic or plastic coated chairs, runners, bolsters, spacers, hangers and rebar supports as required.
B. Inspection of Epoxy Coated Rebars:
1. Coated rebars will be inspected on the jobsite for handling defects, coating abrasion, coating thickness and continuity of coating.
2. Engineer may defer final inspection of rebar coating integrity and repairs until the rebars have been erected and all handling is completed.
3. Repair coated areas as directed by Engineer. Do not place concrete until all repairs to coatings have been completed.
C. Patching of Epoxy Coated Rebar:
1. Patching and repair to be performed in accordance with the instructions of patching material manufacturer.
2. Patching material to provide a minimum film thickness of 5 mils over the bare area. Thickness of area adjacent to patched area not to exceed 15 mils.
3. Areas to be patched to be clean and free of surface contaminants. Treat areas in accordance with patching material manufacturer's instructions before oxidation occurs.
4. Total surface area covered by patching material not to exceed 2 percent of total surface area of the rebar.
5. Rebar welds and adjacent bare rebar areas to also be patched after welding is completed.