Mark,
Most VFDs today post efficiency numbers between 95 - 98% (if you can believe them)... But that's at rated output.
Some years ago, Maury Peltola of ABB, produced some curves for the ACS 500 that I thought were rather interesting. The curves had a very shallow drop-off down to about 30% load at which point the efficiency dropped off quite steeply. Not too surprising if you consider that as the output load decreases, a point is reached at which the fixed losses of the VFD become a greater percentage of the input current draw.
I think you recognize, Mark, that at some point it becomes a numbers game that skews away from reality. Not to digress, but consider a VFD that introduces 47% THiD into a distribution transformer....but at a total amp draw of 5 amps on a 1500 kVA transformer.... how significant is it really.
My previous post, Mark was not an attack upon you as some have erroneously stated. The interrogatories were intend to examine other ramifications over a broader spectrum of applications.
Bottom line: Energy Savings with VFDs .... high probability with variable torque loads. Low probability with constant torque loads. However, in constant torque applications, operating efficiencies may be realized to justy the VFD in the process.
Enjoyed the discussion with you sir.
Kind regards,
jOmega
For instance, consider conveyors with belts... at lower speeds there can be increased frictional losses as more of the belt is in contact with the rollers. At higher speeds, the laws of aerodynamics come in to play and the belt actually lifts off the rollers.
The extruder application.....draws close to 100% torque at 5%-40% speed, at which point the frictional heating of the screw adds to the melt temperature, reducing the viscosity of the material in the barrel; at which point the load drops off with increasing speed.
The energy savings with centrifugal pumps is realized by the elimination of the flow/pressure control valves that are throttled to achieve process operating points. The drop across such valves can be significant.
Positive displacement pumps have little realization of energy savings because they operate in constant torque mode.
Mark, I want to close this with a point that you made with regard to motor losses. In particular the iron and copper losses. That was a concern maybe 10 years ago, but today, with the advent of vector technology...i.e. space vector, voltage vector, etc..... and improved modulation techniques,plus improvements in motor designs, these losses are minimal because the applied current waveform from the VFD is virtually sinusoidal.
I recently made some measurements of several brands of VFDs currently in the market and the data shows that the harmonic content in the output fell within the range of 1.5 - 2.5%. The harmonics occurred a much higher frequencies with very low amplitude than the units of years past. Also, improvements continued to be made in the domain of harmonics introduced into the plant power distribution system. The new Siemens SED2 drive eliminates the dc link inductor, and reduces the bus capacitance to an extremely low value as compared to conventional dc bus topology. As a consequence, the THiD and THvD are extremely low. If you are used to seeing the line current of a typical PWM being two gulps...the SED2 has no distinct gulps. The current is almost continuous because of the small time constant of the dc bus. That is, it begins to draw current from the ac line almost as soon as the line sinewave voltage gets off zero. This has really given cause to VFD designers to re-think the bus topology and yesterday's rationale.