Genieconseil,
Bin method is based on temperature groups and typically includes all hours annually of data for a given city. You need to break out the temperature bins based on the operating hours. Bin Maker (type "Bin Maker Pro" into Google) provides this capability. Next thing how are the units controlled? Are they 100% OA? Are they constant volume? What is the discharge air temperature setpoint during heating? Is there a HD reset sequence? All of these factors will impact how you perform your calculations.
You can calculate sensible energy using the following equation 1.08 * CFM * (Temp IN - Temp OUT). CFM, of course, is the air flow through the unit. Temp IN is the temperature of the air before the heating coil and temperature OUT is the temperature of the air after the coil. You can see now how knowing the operating conditions of you system. If your unit is 100% OA and constant volume with a discharge temperature setpoint of say 80F, then the calc is easy. You get your bin table setup from Bin Maker and set up a calculation in Excel as follows:
1.08 * 25,000 * (80F - bin temp)
1.08 * 16,000 * (80F - bin temp)
Then pull down the calc through the range of temperatures during Outside Air conditions where heating is being provided. The equation will provide you with values in Btu/hr. You will then need to multiply these values in each bin by the hours in each bin to get Btus and then convert into appropriate heating energy units. Also, don't forget the efficiency of the heating system. The calcs you will have performed is the energy to heat the air. How much NG is required to heat that air. You will require approximately 25% more NG, assuming 80% efficiency.
Now, if you have minimum OA and are mixing with return air you will need to modify your calcs. Also, if it is a VAV system... another level of complexity.
Another thing to look at is utility bills. If these units are the only source of heating other than domestic heating look at a couple of years of gas data. Should look like a nice bell shaped curve if you graph it by month with a peak in the Winter and minimum use in the Summer. Take the average of the cooling months (assuming that no heating is performed during the cooling months) and multiply by twelve. This should be a good estimate of the domestic hot water load. If the only remaining load is heating then subtract the calculated domestic heating load from the total utility (keep your units straight) and that will give you your heating load. If the two units are the only other sources of NG use and the units are controlled in the same manner, then just provide a proportionality constant for each unit 61% and 39%. This will provide for a quick and dirty calc and/or a sanity check against your bin calcs.
Good Luck,
Michael Rosenberg