Hi, kssschsekhar
About your question:
"If we energise the transformer from 300MVA side- inrush current/MVA is approx. 10times 300MVA. If we energise the transformer from 150MVA side- Inrush current / MVA: Is it 10 times of 300MVA or 150MVA?"
The answer is:
In general, the LV windings have a cross section area smaller than the HV windings. So, if we energise the transformer via the LV windings the inrush current will be bigger (in pu) than if the transformer is energised via the HV windings.
ScottyUK and davidbeach suggest:
"If you are in a black start condition then make life easy for the generator and close the GCB before energising the field. The excitation system will gently ramp up the voltage to nominal."
My comments is:
That is really a beautfull solution! If this operation is possible, go for it.
Another solution would be to energise the transformer considering a "point on wave" switching strategy, i.e, making a circuit breaker controlled closing at instants at which no inrush currents are produced.
Finally, if you want anyway to energise the transformer by colsing the breaker on the unloaded generator, you will stress both the generator and the transformer with great probability to get overcurrent and/or diferential trips.
Best regards,
Herivelto Bronzeado