Agent, in your experience, typically how close is the period from the model to the approximate period? ASCE table 12.8-1 sets a cap at 1.7Ta for Sd1<1 which means that there are some cases where T>1.7Ta (otherwise there would be no need for the cap). OP's factor is 2.34 which isn't insanely higher than that. The Ta equation needs to be conservative (undershooting the period) and is only based on the system and height. OP's building has long spans which probably make it more flexible than the typical concrete moment frame building of that height. Of course maybe getting such a long period is a sign that something is wrong with the design (ie the spans are too long, the member sizes are too small, the structure wouldn't pass drift limit checks) - I don't have a great feel for that though