When an Architect is designing a new multistory apartment R-2 on a level site with accessible units on the level of exit discharge at what point (number of stories) does the IBC require an elevator to be installed ???
 
Replies continue below

Recommended for you

4 or more stories above or below a level of exit discharge. See 2012 IBC Section 1007.2.1.
 