Are there any 'Rules of Thumb' in regards to the calibration ranges of electronic transmitters ?
I have a process with norm/max values of 100/150psig.
I've asked for a calibration range of 0-200psig (4-20mA) with a normal value at around 12ma and a max value at 16mA.
I also have a range on a temperature transmitter with norm/max process values of 127/149 deg C. I'm ranging the transmitter 0-200 deg C. My boss however says it should be 50-200 deg C. I asked why and he said 'it's always been that way'. I'm quite sure my 0-200 range is just as good as his 50-200 in terms of accuracy etc as we're calibrating modern electronics and not electro-mechanical transmitters from the seventies. Any thoughts, comments ?
Thanks.
I have a process with norm/max values of 100/150psig.
I've asked for a calibration range of 0-200psig (4-20mA) with a normal value at around 12ma and a max value at 16mA.
I also have a range on a temperature transmitter with norm/max process values of 127/149 deg C. I'm ranging the transmitter 0-200 deg C. My boss however says it should be 50-200 deg C. I asked why and he said 'it's always been that way'. I'm quite sure my 0-200 range is just as good as his 50-200 in terms of accuracy etc as we're calibrating modern electronics and not electro-mechanical transmitters from the seventies. Any thoughts, comments ?