Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations TugboatEng on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Electromechanical Totaliser

Status
Not open for further replies.

sonu1978

Electrical
Joined
Feb 23, 2007
Messages
1
Location
IN
Hi
I need to check for an EMT(electromechnical totaliser) disconnection and EMT shorting using only two wires of the coil. How can I do it ??

One end of the EMT is connected to 24V DC and the other end is to a CPLD.
 
Use a series resistor in the low leg to provide a 4.5 volt drop and then use a logic input to monitor this signal. This assumes that the counter will still work with slightly less voltage.


 
If one side of the coil is connected to +24V you can sense the others side of the coil for voltage through a 47K resistor to th base of a transistor. Adding a diode and a 4.7uF capacitor can provide a hold in during pulsing. This will sense a missing counter or open coil.

Running a small current through the coil to make approximately 0.5 volt will allow you to sense an open or shorted coil with a high/low comparator.

Sensing coil kickback might also be a very quick cheap method of determining a functioning counter.
 