For microprocessor relay 50 units I set for 125% of the xfmr low side fault current, with a 3 cycle delay. It takes an extra effort to set the delay for an EM relay.
Transformers at utilities typically don't have many faults, but a few. The distribution system has a few. Lightning, animals, bad drivers, backhoe operators, etc.