Hello sori, I realize I'm going beyond the scope of your OP, but more information would help.
For example, you state:
We plan to start it with a pony motor.
This does not in any way say how you plan to go about this . . .
Would a retired prime mover be partially dismantled to make room for the pony motor needed to be permanently mechanically coupled to the prospective condenser it would drive to synchronous speed?
What kind of pony motor? What rating?
Or would your pony motor be driving a run-up generator similar to what I used to operate?
Or some other approach?
Depending what's already on site, a far cheaper approach could be to segregate a portion of the station's high voltage switchgear so that a two-shaft gas turbine generator rated at, say, 10 to 20 MVA could be electrically coupled to the prospective condenser and used to run it up to synchronous speed.
Alternatively a hydraulic unit at some other site could be segregated onto one circuit or feeder and electrically coupled to the machine for the same purpose.
One electrical area I am aware of found itself in need of a frequency changer between 25 and 60 Hz, and a very innovative approach was developed to address this need, to wit:
Since a great deal more water had been made available to this plant, it was twinned [although its twin had more than double the capacity]. There was therefore now more generating capacity available within the pair of plants than there was water to run them.
So one unit was decommissioned as a generator; the 25 Hz alternator on top was lifted out of the way, the turbine cavity was gutted, and the scroll case inlet and draft tube outlet sealed off with concrete. A new air-cooled 60 Hz alternator small enough to fit into the cavity was then installed, cooling water piped to its bearings and stator cooling rads [to reject the heat from the recirculated cooling air, while eliminating the requirement for a great deal of jack-hammering of structural concrete], and appropriate electrical connections made. The 25 Hz machine was then re-installed atop it and mechanically coupled up.
Starting was accomplished by separating the adjacent hydraulic unit and one outgoing circuit onto their own little synchronizing bus, starting the jacking oil pumps, getting the hydraulic unit creeping, applyiong excitation to both units until the two locked into synchronism, then running them up as a pair, maintaining the appropriate V/Hz ratio on the way to synchronous speed.
It worked beautifully.
Going one step further, the system design engineers did not want to be limited to starting only from the 25 Hz side, thus the ability to perform starts was specified for the 60 Hz machine as well so the unit could be started from the adjacent 60 Hz plant.
Addition via edit: since the frequency changer was kept i/s 24/7 and very rarely shut down, there was little additional burden imposed by system reconfiguration for these infrequent starts, and therefore very little financial incentive to develop a different starting means such as adding really beefy amortisseur windings to either of the machines so as to enable DOL starts.
Bottom line is, there may be any number of ways to not needlessly spend money and still accomplish your desired objective . . . more information yields better answers!