Regarding electrical conduit in Post-Tensioned Slabs. ACI 318 section 6.3.5 addresses conduit embeded in concrete. However, I am looking for guidelines/provisions for clearance and/or tolerance between electrical conduit and PT anchor zones or PT cables in general.
I am familiar with the common detail for vertical penetrations near tendon anchorage zones (shedule 40 pipe when vertical pentration is in the anchorage zone, etc.).
However, this condition is when an eletrical conduit runs perpendicular or parallel to the anchorage zone or to the tendons in the plane of the slab.
I have a condition where a contractor has installed a number of electrical conduits running through our PT anchor zones in both primary directions. We have requested that the contractor avoid the anchor zone, but we have no reference/provision for clearance between the anchor zones and conduits or between parallel tendons and conduits in general.
I certianly would appreciate any assistance regarding the matter.
DesignIntegrity
I am familiar with the common detail for vertical penetrations near tendon anchorage zones (shedule 40 pipe when vertical pentration is in the anchorage zone, etc.).
However, this condition is when an eletrical conduit runs perpendicular or parallel to the anchorage zone or to the tendons in the plane of the slab.
I have a condition where a contractor has installed a number of electrical conduits running through our PT anchor zones in both primary directions. We have requested that the contractor avoid the anchor zone, but we have no reference/provision for clearance between the anchor zones and conduits or between parallel tendons and conduits in general.
I certianly would appreciate any assistance regarding the matter.
DesignIntegrity