The line of sight must be from the disconnecting means to the STARTER or control panel. If this is a package system, I'm assuming the starter is located at the compressor skid.
NEC also requires a local disconnect at the motor, but there are exceptions to this that you are probably aware of.
NEC does limit "in sight" to 50 feet, regardless.