7anoter4,
I appreciate the valuable information you have provided. My next question is about modeling this in a grounding calculation program, in particular, CDEGS. Since you mentioned that resistivity of Bentonite increases when dry, my concern would be modeling a ground well with 2.5 ohm-m resistivity for Bentonite.
Jghrist,
Could you advise on how you would model a ground well in CDEGS?
sjmgd977,
I do have green book and IEEE-80. The station I am doing a study for is a pre-existing Utility substation and has plenty of 10 ft ground rods. It currently can withstand 25kA but we are trying to inject 50kA instead. My next approach is to try ground wells since the resistvity of the station drops to about 10 ohm-m after 7 ft of depth and the surface resistivity is around 150 ohm-m. Also, I am not sure about how economical chemically treating the soil would be since the station is about 600 ft x 500 ft. However, I am interested if you can convince me otherwise.