Hey Keith, I wasn't taking credit; I was merely trying to make a subtle statement about gratitude...& FWIW going diode wouldn't have been my choice, either; if anything I would add my concurrence to che12345's ringing endorsement of your recommendation.
The only minor tweak I might have added is that if a transformer with a choice of both input and output taps was used, following commissioning I'd monitor for a week to ten days and see what sort of more-or-less standing delta T was achieved, which, if inadequate, would suggest selecting other taps to give just a smidgen more [or maybe less] of anti-condensation heat.
OP says 240VAC is what's available; if wired to the 380V hi-side terminals, would the upset in V/Hz ratio be of any consequence? Perhaps not in a transformer of such low rating?