It is not clear what you are trying to do. The distances between facilities and elevations have also not been provided.
As far as flows go, if you have a normal house residence, you can figure 350 gpd average flow per house, and a peak flow of 4 times that.
If you have six houses on one line, that would be 2,100 gpd average flow, and a peak flow of 8,400 gpd.
A 4" diameter building sewer on 1/4" slope per foot can hand 216 fixture units. A 4" diameter building sewer on 1/4" slope per foot flowing half full will discharge approximately 76,900 gpd.
A normal residential bathroom consists of 6 fixture units. One fixture unit equals about 35 gal per 8 hour.
A building sewer is defined as that part of the building drainage system that extends from the septic tank or a public sewer to a point 3 ft out from the foundation wall. Separate sewers are generally required for new construction.
Most areas have regulations that require a minimum size of 8 inch for public sewers.
However, if all of your development is a private system, then a 4-inch diameter sewer from the septic tank is adequate for the flow. As far as cleaning goes, going to a 6" is probably not going to help much. Lower flows in the larger sewer may cause solids to drop out in the sewer.