siboatyard
My experience with replacing older motors for more efficient motors is that it only pays back for equipment that is used for a large number of hours per year (at least over 50%). There are two good motor payback analysis tools that I use, one is Baldors BEST 2.0 available at
and the other is MotorMaster 4+ available at
Efficiency of motors at part load isn't as bad as most people think. You cant look at amps because the power factor is much worse at part load and most people can't measure power only amps. See
If you are really interested in compressed air efficiency see AirMaster at the same link that MotorMaster is at. There is also the Compressed Air Challenge Sourcebook at
sterl
1)No arguement here. I will just add that the efficiences of the compressor at slide valve positions less than 50% is much less than near 100%. Also air compressors (as mentioned by
siboatyard usually operate somewhat differently than refrigeration compressors since air compressors usually are controlled on discharge pressure and refrigeration compressors are usually controlled on suction pressure. The capacity control mechanisms are usually different.
2) See what I said in response to
siboatyard.
3) That is a good idea although on a refrigeration compressor I doubt that the (ambient) air will get heated much more than normally happens.
4) I think you combined your air compressors and refrigeration compressors in this one. I have never seen a discharge pressure regulator on a refrigeration system since it would only waste energy and most systems don't have desuperheaters although I have seen them. I was just going to put a flowmeter (probably a differential pressure type like an Annubar) in the discharge line of the compressor and calculate mass flow by measuring velocity and compensating for temperature and pressure since these are measured by the compressor control system. I don't see any reason that won't work although I might not get 10 pipe diameters of straight pipe. Usually there is about 5 - 10' of pipe between the discharge flange of the compressor and the discharge header where the other compressors are connected into the system.
5) The machines are over 15 years old. I did get a response finally from a major (refrigeration) screw compressor manufacturer and they told me that screw compressors loose very little efficiency since the rotors never touch the housing and are sealed by the oil. They said that even if debris or liquid slugging damages the rotors they loose only 5 - 10 % efficiency. So I think that I won't bother trying to measure the refrigerant flow and give up on trying to get a utility rebate on the refrigeration compressor replacement (unless of course the new compressor is just more efficient than the old compressor was in new condition).