There was a great confusion in ASCE 88 about what is called a tributary area when calculating pressure coefficients. That was wrong they should have never called it tributary area because we all know what is a tributary area. however, ASCE 98 is very clear now in calling it effective wind area. I am reviewing a design by other Engineer and I believe he did not use the right value for the effective wind area. Let see if you can agree with me.
A Tower 109 feet heigh 90' long by x 81' wide. The engineer used an effective area that is less than 10 sf to calculate GCp (external pressure coefficient for the roof). I beleive this is wrong. Way over design. We all know the smaller the effective area the higher is the pressure. I believe the effective area of this building is based on whether the roof slab is one way slab or two way slab. If it is one way slab the effective area should be 81'x 81'/3=2187sf; if it is two way slab the effective area is 190'x81'= 15390 sf.
Let me hear from you before I redesign. Thanks in advance.