Ron,
The British and European codes state:
"Concentrated loads
The bending moment arising from a concentrated load may be distributed over a width of slab equal to the width of the load plus the lesser of the actual width or 1.2(1 - (x/l))x on each side of the load, where x is the distance to the nearer support from the section under consideration, and l is the span."
This is recommended for RC slab but there should be no difference for a PT slab. With a long span the above effective width can get quite large, i would place an upper limit of the column strip width on the effective width.