Um, I think I already addressed your points in my last post. But just in case: realize that with FV, your motor will take something like 6 seconds to start. With the reduced-voltage starter, it will be longer -- I don't know how much longer, but I bet less than 15 seconds. A Google search or the Red Book or PowerTools would probably shed more light on the starting time if you're that concerned. But NFPA is cool with the starting time. No mechanical mods required, use a listed controller and limit the voltage drop per 695.7 and you're good to go.
You mentioned soft-start -- if you're talking about a solid-state soft motor controller, I don't believe such controllers are listed for use with fire pumps, but I could be wrong. If anyone knows otherwise, please clue me in. I believe most reduced-voltage fire pump starters are autotransformer type or some other "old-fashioned" induction type. Anyone who's ever used a computer realizes that the last thing we need is a digital control system in charge of life safety equipment (how many people will I piss off with that one?!?). KISS (Keep It Simple Stupid) is the name of the game in life safety.