We have five different applications of 13.2kv motors with surge capacitors, instantaneous ground relay ("50G", electromechanical relay fed from window CT enclosing all three phases). No intentional delay. Fed from HRG system. Been operating many decades without spurious trips.
I hadn't stopped to think about this aspect before (at least not recently enough to recall).
During across the line start, how to analyse capacitor currents. As a first simple model, I'd be inclined to say that all three phase to ground voltages ramp up to their prescribed value in the same delta-T. Assuming the three phase-to-ground voltages sum to zero, the computed dv/dt's under above assumption would also sum to zero. But didn't consider things like LC ringing (rather than smooth ramp), CT saturation, non-simultaneous closing, etc which could throw a wrench in the works.
Any thoughts to further describe this? Does anyone have links to literature describing adjustment of instantaneous ground setting for capacitor "inrush" currents.
=====================================