I would appreciate any feedback regarding the negative effect of increased inlet water temperature into a cooling jacket surrounding a mixing machine.
My company uses a mixing machine that mixes together various dry powers in the manufacturing of brake shoe friction material. The mixing shaft assembly of the mixing machine is surrounded by a water cooling jacket system. The outlet temperature of the mixed material is about 180F; inlet temp is ambient.
Currently the inlet water temp to the cooling jacket is 45F; leaving water temp is 52F. Water flow is 9 gallons per minute. I can use the equation qw = 500 Qw dT to calculate the heat transfer into the water at about 31,500 Btu/hr.
qw = heat transfer rate to water in Btu/hr
Qw = water flow in GPM
dT = water temp increase across unit
This setup currently works fine. However, I have been asked if we can use cooling tower water as a the cooling medium rather than the chilled water we currently use. The temperature of the cooling tower water is 89 F maximum. Available water flow is more than 9 GPM.
Is there any method to calculate if the 89F water will provide equivalent cooling effect as the 45F water? I know the flow would have to increase, but flow can only be increased by so much.
My company uses a mixing machine that mixes together various dry powers in the manufacturing of brake shoe friction material. The mixing shaft assembly of the mixing machine is surrounded by a water cooling jacket system. The outlet temperature of the mixed material is about 180F; inlet temp is ambient.
Currently the inlet water temp to the cooling jacket is 45F; leaving water temp is 52F. Water flow is 9 gallons per minute. I can use the equation qw = 500 Qw dT to calculate the heat transfer into the water at about 31,500 Btu/hr.
qw = heat transfer rate to water in Btu/hr
Qw = water flow in GPM
dT = water temp increase across unit
This setup currently works fine. However, I have been asked if we can use cooling tower water as a the cooling medium rather than the chilled water we currently use. The temperature of the cooling tower water is 89 F maximum. Available water flow is more than 9 GPM.
Is there any method to calculate if the 89F water will provide equivalent cooling effect as the 45F water? I know the flow would have to increase, but flow can only be increased by so much.