I have kept the foundation at 18" because this building is built adjacent to exiting building with foundations at the same depth.
Correct, the CMU wall along this line, a total of 20 ft long, is the most eccentric element. The glulalm spacing is 10ft, one beam at each end of the wall and one in the center. The roof glulam beam at this wall location will be supported by this wall. The floor glulalm beams will be supported on a masonry pilaster to assist in moving this reaction farther away from the property line. A pad footing will be provided at the glulam locations. These footing will be part of a combined footing system that is connected to interior columns that are 19 feet away from the exterior face of the masonry wall. The combined footing will redistribute the eccentric loads, as well as, the torisional forces from the eccentric wall (transmitted from the narrow stip footing) between these locations. I find the span short enough to numerically justify that the short span of eccentric wall footing, approximately 6 feet in length (designed to spand the full 10ft of the combined footing), will be sufficiently stiff to transmit the torisonal effect from the eccentricity of the wall to the pad footings. The footing width shall be determined by an assumed uniform bearing pressure underneath. For lateral forces, parallel to the wall, the total "I" shaped wall foundation configuration shall be utilized.
the total gravity load, live and dead is approximatley 2.31 klf. The wall dead load is 90 psf (8 inch fully grouted) * 24.5 feet = 2.205 klf which governs the design. per the calcs, a 24"x18" wide cont footing with 3-#5 T&B and #4@12 ties is sufficient to transmit the eccentric wall loads to the pad footings. This is for gravity alone.
I agree in using the 5" sog to restrain the footing is unacceptable. It will difficult to develop sufficient rigidity within the masonry wall - 8" with #5. Will investigate more. It is a great suggestion. I think the concept to transmit the eccentric forces via torision to the combined footings provides the clearest load path.
I really appreciate all your feedback. Thank you! This is my first eccentric wall foundation. I wish there were more design examples that fully illustrate these concepts - tied foundations and the resultant bearing pressures from utilizing fixed fixed beams to transmit eccentric loadings, foundation pressures by restraining the footing from rotation via a reinforced concrete slab on grade, and foundation bearing pressures via restraining the footing rotation at the wall. Maybe someone can write a book titled "Foundations - from the classroom to office".