We are using Eaton's Microprocessor programmable feeder protection relay EDR-5000 as attached. The swgr factory had switched relay coil B connections as shown in the attached.
We are using the relay as simple phase and ground overcurrent relay. No voltage input and no directional settings.
The relay measured large ground current IX, and showed large calculated ground current IR. The relay tripped the breaker 3 times with timed ground measured current IX, during magnetizing inrush during commissioning. IR trip was deactivated, so that did not operate relay.
It was surprising that once we found and switched the B coil connection to make it right, both IX and IR magnitude dropped considerably during magnetizing inrush and breaker did not trip for next 7 to 8 operations until now. No relay settings were altered.
It is understood that magnetizing current will keep on changing depending on where the breaker contact closes in the sine wave cycle. The IX and IR value will also change with this during magnetizing inrush. But I do not think that the IX magnitude is the reason (or only reason) for breaker tripping.
Question: The big change in IR, calculated ground current, is understandable. But I cannot understand the big change in IX measured value, after B coil connections were switched to make it right. It seems IX value should not be impacted much whether relay B coil is connected right or reversed as shown. Somebody familiar with relay internals can explain the relay behavior.
Thanks in advance.
Thanks in advance.