Rodmcm
Electrical
- May 11, 2004
- 260
If you look at many generation plant connections from MV to HV then the MV (say 11kV) bus is often unearthed until the generator synchronises.
The popular idea is that there is no earth return from the MV to the HV and hence, no fault current, no step and touch potential issues, and little man safety risk. The usual protection is a broken delta or neg seq voltage to detect an earth fault.
This makes me nervous, as inherently I do not like any unearthed systems at high voltages. It is easy to create a managed earth with an zig zag transformer or similar.
So, looking at it from a pure safety point of view, is there a risk? Is there any possibility for earth return current, and how would you calculate it or assess the risk?
Also, I would be interested in views on broken delta protection. A protection engineer I know thinks they should be avoided at all costs!
Interested in the thoughts from the collective wisdom of this forum
The popular idea is that there is no earth return from the MV to the HV and hence, no fault current, no step and touch potential issues, and little man safety risk. The usual protection is a broken delta or neg seq voltage to detect an earth fault.
This makes me nervous, as inherently I do not like any unearthed systems at high voltages. It is easy to create a managed earth with an zig zag transformer or similar.
So, looking at it from a pure safety point of view, is there a risk? Is there any possibility for earth return current, and how would you calculate it or assess the risk?
Also, I would be interested in views on broken delta protection. A protection engineer I know thinks they should be avoided at all costs!
Interested in the thoughts from the collective wisdom of this forum