pittengineer
Electrical
- Aug 23, 2009
- 31
I have been requested to perfrom an earth resistance test here at our industrial facility. This tested is mandated by MSHA requirements that govern our site.
Our distribution voltage is 4.16kV and our utilization voltage is 480V.
I have been researching this test and plan on performeing a 3-point fall of potential test. I plan on following the IEEE 81 standard as the guidelines for this test and the acceptance results will be a result of less than 5ohms as stated by NETA.
Our site is laid out as such that we have a utility substation located on-site at our plant, and then have several electrical rooms throughout the plant which have various unit subs, MCC's, swgr etc... Each of these electrical rooms has a ground ring around it with various parts of the ring being connected to the equipment inside each room. The various grids around each room are connected together through copper in ductbanks etc.. to create the ground grid for the plant. A couple of questions regarding this test.
1) Since all of the electrical room ground grids are tied together do I need to perform this test at each individual room or just perform in one location? How is this typically handled when multiple grids are tied together such as in a large facility?
2) Do I even need to pefrom this test at the electrical room ground grids, or can we just do one fall of potential test at the utility substation and check that everything is connected back to it? Would this sill ensure the LV side of the grid for each of the unit subs in the electrical rooms?
3) Once a ground reference is establised I plan on having a 2-point test performed between the ground reference and all the associated equipment such as transformers, mcc's, vfd's, etc... I am going to follow the NETA standards of less thatn .5ohms for this test. Other than this 2-point test, is there anything else that should be included with this testing procedure?
4) We perform ground continutiy checks on motors and equipment routinely. Is there a standard for guidance on methods for performeing ground continuity checks, and equipment bonding checks?
I was hoping that maybe someone here had experience with performing these test in a large enviornment such as mine.