The short answer is: avoid putting anything much more than absolutely required on the GFI (RCD) device.
The long answer is:
1. I made the mistake of wiring a fluorescent fixture in my kitchen to a GFI outlet. Flipping the switch on will trip the outlet once in a while. It never trips after it has started, only instantaneously with starting. This happens only about once every month or two, not every day. I cannot explain why the starting current would not be equal on the phase and neutral, but apparently there is some small difference there about equal to the trip level of the receptacle.
2. Every device has some small associated ground leakage current. Every device you add to a GFI circuit will add to the total ground leakage seen by that circuit. It does not take too many downstream devices leaking at maybe 3 to 10mA to add up to 30mA, and start causing a bunch of nuisance tripping. This effect is exacerbated in areas where water can condense, such as cold rooms, bathrooms and outdoors (generally, most of the places where you are required to provide GFI).