bass1mj
Electrical
- Aug 15, 2002
- 11
Does anybody have experience with regards to the use of earth leakage protection devices in a VSD installation. We are using a resistance grounding system (IT-system) on our MCCs and need to use Earth Leakage protection on all feeders from the MCC. With the VSD installations, however, we have found that the devices do not operate due to the high frequencies that can be evident on the output of the VSDs. Normal VSD ground fault protection will also not operate as fixed resistor are used in the VSD to determine ground fault setting and this is higher than the earth fault current permitted to flow by the NER.
I found a device by Littlefuse on the net, but would also like to know if anybody have used other makes.
I found a device by Littlefuse on the net, but would also like to know if anybody have used other makes.