For a line-to-ground fault on the secondary of 1.0 per unit, there will be current in two of the three phases of the primary of only 0.58 per unit. This is why it is difficult to provide adequate through-fault protection for delta-wye transformer from only the primary side.
There will be no ground current on the primary, only phase current, so any ground fault protection on the primary will not see the fault.