i want to explain more ..
a sqirel cage induction motor 400v , delta winding, 110kw.
this motor protected by an earth fault relay with a core balanced CT. when measuring the isolation resistance of the motor, it founds high (>1 G ohm for 1 min),but at the start of the motor the earth fault relay tripped (I=0.6A , delay time=0.6sec). i have to increase the delay time to 2.4sec to prevent the trip at the start of the motor. what is the cause of the appearance of the residual cauurent at the start of the motor. i knew that the motor spend about 6 monthes without operation .. the motor doesn't have a space heater.