In light of "withdrawn" IEEE Std. 565, I understand that EEC is required for single point bonded cables for the following reasons:
1- Equalizing sheath voltage at both ends to avoid transferred voltage issue.
2- Reduce the potential gradient around cable jacket for through faults esp. with high resistivity soils (I think a bare conductor will do better here!)
3- Reducing sheath returning current
the double point and cross-bonding don't require that; however, I think it will still suffer the voltage gradient issue in case of a fault return path nearby the cable.
Other issue is that sheath may be used as a path for fault currents / through faults.
Why ECC not required for double point and cross bonding cables?
1- Equalizing sheath voltage at both ends to avoid transferred voltage issue.
2- Reduce the potential gradient around cable jacket for through faults esp. with high resistivity soils (I think a bare conductor will do better here!)
3- Reducing sheath returning current
the double point and cross-bonding don't require that; however, I think it will still suffer the voltage gradient issue in case of a fault return path nearby the cable.
Other issue is that sheath may be used as a path for fault currents / through faults.
Why ECC not required for double point and cross bonding cables?