OK, I'm getting more confused - maybe someone can help even more. Would the forces generated by slug flow be applied only in the same direction as the fluid flow? Specifically, when the fluid reaches an elbow, does the force only apply at the elbow inlet or does a force of equal magnitude develop at 90 degrees to the inlet?
Additionally, would the only force applied to an external support be due to slug flow? I am thinking that the stresses developed due to water hammer, etc. would be restrained by the piping walls and fittings and not transferred to supports. Am I totally off base?
The specific problem at hand is a fire protection deluge system ring header supported off pipe stanchions. We have designed several such systems where the ring header is located several feet above a floor. When the system discharges, the piping loop shakes initially (as expected), but no failure is experienced. However, when the approving authorities see the system shake, they want these shaking forces accounted for in a structural calculation.
Recent additions of NFPA 15 (National Fire Protection Associations Standard for Water Spray Systems) offer guidelines for sizing such pipe stands, but it appears as if they are only sized for the load due to water filled piping, not dynamic loads.
Being a sprinkler system designer, I don't have access to any of the pipe stress analysis software recommended earlier, but if slug flow is the only significant contributing force, I think I can do hand calcs to approximate such loading.
Any suggestions?