davefitz
Mechanical
- Jan 27, 2003
- 2,927
Kindly advise if you can provide a reference that describes how to determine the dynamic sensing error of a pressure sensor with long narrow sensing tube.
IN our application we have a large coal fired furnace. The furnace pressure ( "draft")is sensed by a pressure transmitter, but this transmitter is separated from the furnace by a 30' long x 1" dia sensing tube. Large changes in furnace pressure ( from 14.7 psia to 13.7 psia ) , as during a main fuel trip at full load, are predicted to casue a 1 psig drop in pressure within 2 sec but the sensor is not detecting more than a 0.5 psig drop in pressure.
I hope I don't need to make a 1 dim finite diff model to determine this error- this type of error must have been addressed by now.
IN our application we have a large coal fired furnace. The furnace pressure ( "draft")is sensed by a pressure transmitter, but this transmitter is separated from the furnace by a 30' long x 1" dia sensing tube. Large changes in furnace pressure ( from 14.7 psia to 13.7 psia ) , as during a main fuel trip at full load, are predicted to casue a 1 psig drop in pressure within 2 sec but the sensor is not detecting more than a 0.5 psig drop in pressure.
I hope I don't need to make a 1 dim finite diff model to determine this error- this type of error must have been addressed by now.