dust detection

Status
Not open for further replies.

clarke

Electrical
Aug 6, 2003
26
i need to detect when dust is present in an exhaust stack and was wondering if anyone knows of any probes or sensors that could be used. I have heard of using triboelectric sensors but these are exspensive and seem to be abit ott for what i want. I have tried using a differnetial pressure switch to monitor any change in pressure between clean and dirty side of the filter when we get a ripped filter bag but there wasnt any significant change in pressure so therefore it didnt work, but i am willing to listen to any suggestions.
 
Replies continue below

Recommended for you

Gooogle up "opacity meters", They come in sizes for smoke stacks to exhaust pipes for diesel trucks. Most use a light source that shines through the dust/smoke.
 
A common problem. A great solution is specular reflection, just like fog horns work, and they need to be accurate.

A light is flashed and if more than X amount of back-scatter is detected by a sensor next to the lamp, then there is fog = run horn.

You can use this same method in a stack. You set up the light, and a receiver next to it, and then run a permanent purge air into the barrel of the instrument to prevent any contamination of the sensors.

Someone must make this.

Keith Cress
Flamin Systems, Inc.-
 
There are systems that detect when a standard HVAC filter is dirty and needs changing. These use pressure sensors that measure full-scale pressure difference of only a few inches of mercury. Your exhaust stack system is not quite the same, but when you tried differential pressure, did you try a sensor with a very small full scale range?
 
Thanks comokid the filter typically runs at 13millibars obviously this changes between clean and dirty but for the purpose of what i was doing i used a 0 to 15mbar guage and then set the switch to sense if the pressure dropped below 13mbar. There was no cange of pressure shown on this gauge when the bag was split(cut a hole in the bag with a knife) and the switch didnt pick it up either, the switch was a dwyer series 1910 with a dwyer magnehelic gauge. Dont know if you have any ideas why it didnt work but would appreciate any input.
 