I have a question regarding calculating pull over capacities for TEKS screws. According to ESR-3223, Table 3 - Allowable Tensile Pull-Over Loads, the allowable tensile pull-over load for a #12-14 HWH screwed into an 0.048 inch thick steel sheet equals 619 lbf. However, according to AISI S100-07 Section E.4.4.2, the pull over load, Pnov/omega, is as follows:
Pnov = 1.5*t1*d’w*Fu1 where
t1 = 0.048 in.
d’w = dh = 0.4 in. Case (B)
Fu1 = 58 ksi (as indicated in footnote 3 of ESR 3223, table 3)
Omega = 3
Therefore,
Pnov/Omega = (1.5 )*(0.048 in.)*(0.4 in.)*(58 ksi.)*(1000 lbf/k)/3 = 578 lbf
This is not equal to 619 lbf. Now according to ESR-3223:
“ITW Buildex TEKS Select Structural Fasteners are recognized for use in engineered connections of cold-formed steel construction. Design of the connections must comply with Section E4 of AISI S100."
I therefore do not understand why the values are not matching. Please explain to me why. Thanks for your consideration.
Pnov = 1.5*t1*d’w*Fu1 where
t1 = 0.048 in.
d’w = dh = 0.4 in. Case (B)
Fu1 = 58 ksi (as indicated in footnote 3 of ESR 3223, table 3)
Omega = 3
Therefore,
Pnov/Omega = (1.5 )*(0.048 in.)*(0.4 in.)*(58 ksi.)*(1000 lbf/k)/3 = 578 lbf
This is not equal to 619 lbf. Now according to ESR-3223:
“ITW Buildex TEKS Select Structural Fasteners are recognized for use in engineered connections of cold-formed steel construction. Design of the connections must comply with Section E4 of AISI S100."
I therefore do not understand why the values are not matching. Please explain to me why. Thanks for your consideration.