Dual voltage rating
thinker
I would like to understand why the same cable has dual
voltage rating: UL/CSA/TC: 600V and UL AWM 1000V. I am
wondering now what is the actual voltage the insulation
is designed to withstand? (To be more specific, I mean
the OLFLEX part number 760204).
In a 0.6/1KV cable the first rating is the phase to earth rating, the second is the phase to phase. In a three phase system there is a ratio of sqrt(3) between the phase to earth and phase to phase rms voltages.
Suggestion: 1000V/sqrt3=577V
1000V is the limit for low voltage systems. Practically, the system low voltage within the power distribution system ends with 600V level (or Class). See IEEE Std 100 "Dictionary" or ANSI 84.1-1977 for Voltage Classes
TC 600V intended for cable tray installation of premises wiring per NEC Article 318.
AWM 1000V ‘appliance wiring material’ — AWM wires are intended as factory installed or factory provided components of complete equipment submitted for investigation, rather than for direct separate installation in the field. {One example is ballast-to-lamp wiring at 750V.}