Kevin,
I guess you already have the flow element, and you are just trying to get the best rangeability from it? So replacing it with another type of flowmeter may not be practical if you cans shut down the line.
You have not given us any flow rates, pipe sizes, pressures or temperatures, so it is a little difficult to give a complete answer. But A word of warning. Flowmeter manufacturers claim turndown figures that are completely unuseable. For example vortex meters (which are velocity devices) are designes with a meter max of up to 130m/sec. They may claim 100:1 turndown, but on compressed air it is undesireable to to have high pressure drop so your ideal max velocity sould be 12m/sec. This would leave you with a useable turndown 12/(130/100) =9.2:1 No better than 2 DP transmitters! And their answer to this may be to reduce the pipe size and create a pressure drop that your compressor will burn fuel trying to overcome.
To give a reasonable answer to your question, Lets answer it in three parts.
Firstly you should split the range of the transmitters based on the turndown of flow that you require and not the turndown of DP. Orifice plates etc have no moving parts, so the square law will follow all of the way down to 0% (according to ISO5167). So the problem lies in accurately measuring the DP producds.
Secondly the transmitters you select for the upper and lower dp measurement should have different measureing cells, because the lower reange unit needs to have greater accuracy,sensitivity and stability.
Thirdly, the chageover point is normally the point that causes the problems. If you use a switching point, then you will get a step change in the signal. Some flow computers avoid this by phasing one signal in and the other out within a change over zone. The easyest way to achieve this is to scale the input signals to flow units before the changeover. Set up your phase zone and then use a weighted average of the two signals within the zone.
If you have a PLC or DCS this will be possible with some maths. If not you may want to go down the flow computer route.
I trust this helps,
Mlv