Don't have 2002 handy, but I'm sure you have the idea for the overhangs.
A 6' dry sprinkler would not be my cup of tea. Like a vertical sprig, you'll have to restrain the barrel. Call some wholesalers for pricing...try not to fall out of your chair when you get the quote.
A dry sprinkler is essentially a pipe nipple with a sprinkler at the end. At the end opposite the sprinkler, there is a plug sealing the barrel, connected thru to the heat sensitive element of the sprinkler. When the sprinkler pops, plug drops and water flows...hence "dry sprinkler".
By virtue of this, the barrel has to extend from the sprinkler down into the warm area a sufficient length (victaulic has some nice literature on sprinkler barrel length). The fitter has to either have his branch line hung, or be pretty damn sure of his elevation before you order up the sprinks.
In your attic situation, your branchline would run in the warm space, with a pipe nipple made into the o'let, 1" tee made on to the nipple, with your dry sprinkler made into the opposite leg of the tee. A 1" plug is made into the tee's outlet. Sounds a bit strange, but if you look at the thread of a dry sprinkler, it's long enough that when fully made into the o'let, it will extend down into the water stream.
No air compressor, dry sprinkler is a sealed unit. Hope I was clear enough. 8.4.9.1 is new for 2010. States " Where dry sprinklers are connected to wet pipe sprinkler systems protecting areas subject to freezing temperatures, the minimum length between the sprinkler and the fitting shall be in accordance with the manufacturers instructions."