I make mistakes every single day; I run into beams I didn't see on the drawings, sometimes hit lights, hit HVAC ducts often enough but big deal, that's why fitters carry cutters, threaders and groovers. I try to keep my mistakes to a minimum but try as hard as I can I still make them. So what?
But the one mistake I do not make is the flow test. I started laying out sprinkler systems 35 years ago next month and the only time a job has scared me is when there was a difference between the flow test figured for the job and the actual flow test conducted after we got the job.
Running into a duct might cost $300 in labor and material but having not having enough water could cost enough to retire.
Before I did anything on this project I would conduct a flow test. I would invest $500 in a flow test kit (have your gauges certified), get the local fire official to help/witness and carefully document it with dates, times and get signatures of everyone there. I insist on conducting my own flow test using my certified gauges unless the AHJ will give it to me in writing on their letterhead.
You are laying out a 6" DCA which is going to be the smallest size but this thing is going to be 8" or even larger.
It isn't impossible but I will be surprised if this building doesn't require a fire pump.
We're talking about compressors so this is a dry pipe system, right? My first thought was ESFR K25 but the dry system knocks that out.
It does appear you need one level of in rack sprinklers using large drop but IMO that is the least of your problems. Based on Table 12.3.2.2.1(a) (2002) you are going to need a theoretical minimum supply of (25+(25^.5*11.2)+500=1,900 gpm not counting the in rack sprinkler or the additional water required to balance the system. Using large drop this job is going to end up needing 2,500 gpm and that is a lot of water. I will be surprised if the city can deliver this, you should think in terms of a 10" feed and DCA and, most likely, if you are lucky, a 1,500 or 2,000 gpm fire pump. Most likely (95% chance) the city doesn't have the water to supply the pump @150% so you are looking at a 150,000 to 200,000 gallon tank @ $1.00/gallon. Then the pump room (larger than 8'x8' I can guarantee you) and don't forget the boiler to keep the tank from freezing and tell the owner to enjoy his $15,000 per season heating bill that goes on forever.
Given the small size of this building the owner will have more tied up in the fire protection than they will the building.
And someone is pushing you for a "guess" on this?