I'm working a lot with the analysis of existing and design of new drilled pier foundations for telecom tower footings. Very light axial loads and relatively high lateral loads. The foundations are typically modeled in LPile.
The foundation section of the tower code, TIA-222 (Section 9.4 for Rev G & 9.7 for Rev H) has a Φs factor for design. For piers this factor is 0.75. The corresponding note says, "For foundation analyses which model the lateral stiffness of the soil, factored reactions for the analysis shall be divided by Φs."
ACI 336.3R-14 in section 4.1 states, "Normally, service loads are used to calculate the resulting moments, shears and axial forces, which are then multiplied by the appropriate load factors for the various cases of loading for structural design of the pier."
The two approaches seem to contradict each other. I'm not sure I agree with modeling soil structure interaction using factored loads that area again factored up. What useful information does this model provide? Deflections are meaningless. Forces in the member may not be accurately represented as the soils will behave differently under different magnitudes of loading.
If I were not working within this TIA code, I would model as the ACI document indicates and factor resulting forces for RC pier design.
For now, my approach is to model with (3) load cases: factored-factored loads, unfactored loads, and TIA service loads (lower wind speed). I take the member forces from the unfactored loads, factor them up (including the Φs), then compare to the output from the factored-factored load case and use the worst for design.
As for deflections, Rev. G indicates that deflections can be ignored if the TIA service load case at grade deflections are less than 0.75" which is typically the case. The factored load deflections are unreasonable and often multiple inches.
Does my approach seem reasonable? Anything else any of you would consider?
The foundation section of the tower code, TIA-222 (Section 9.4 for Rev G & 9.7 for Rev H) has a Φs factor for design. For piers this factor is 0.75. The corresponding note says, "For foundation analyses which model the lateral stiffness of the soil, factored reactions for the analysis shall be divided by Φs."
ACI 336.3R-14 in section 4.1 states, "Normally, service loads are used to calculate the resulting moments, shears and axial forces, which are then multiplied by the appropriate load factors for the various cases of loading for structural design of the pier."
The two approaches seem to contradict each other. I'm not sure I agree with modeling soil structure interaction using factored loads that area again factored up. What useful information does this model provide? Deflections are meaningless. Forces in the member may not be accurately represented as the soils will behave differently under different magnitudes of loading.
If I were not working within this TIA code, I would model as the ACI document indicates and factor resulting forces for RC pier design.
For now, my approach is to model with (3) load cases: factored-factored loads, unfactored loads, and TIA service loads (lower wind speed). I take the member forces from the unfactored loads, factor them up (including the Φs), then compare to the output from the factored-factored load case and use the worst for design.
As for deflections, Rev. G indicates that deflections can be ignored if the TIA service load case at grade deflections are less than 0.75" which is typically the case. The factored load deflections are unreasonable and often multiple inches.
Does my approach seem reasonable? Anything else any of you would consider?