There is an interesting mathematical excercize to find the location of max efficiency if we ASSUME that the losses are divided into two categories:
A - losses that are constant with respect to load
B - losses that vary with load^2 (I^2*R losses vary approximately with load^2 at high load... at lower load the approximation is not as good but will not matter if we're evaluating behavior at high load).
This suggests the model:
L = A + BX^2
where
L = total losses
X is power as fraction of full load power
A is no-load losses, excluding small losses due to stator I^2*R at no-load
B is load-related losses at 100% power (total 100% power losses minus no-load losses)
How do we maximize efficiency = Pout/(Pout+L)
where Pout =X*P100 and where P100 is rated output power
This should be the same as minimizing the inverse.
ie. minimize 1/effic. = (L+Pout)/Pout = L/Pout + P/P = L/Pout+1
The 1 is a constant and doesnt affect the minimization.
=> minimize L/Pout
minimize: L/Pout = [A + B*X^2] / [X * P100%] = [A/X + B*X] / P100
Since P100 is a constant with respect to X, it doesn't affect the minimization.
=> minimize [A/X + B*X]
Set derivative =0
d/dx{[A/X + B*X]} = [-A*X^-2 + B] = 0
A*X^-2 = B
A = BX^2
Xpeak=sqrt(A/B)
IF no-load losses were half the total losses, then A=0.5, B=0.5, peak efficiency would occur at 100% load.
Typically no-load losses are a smaller fraction. Let's say A = 0.33, B=0.67, then X = sqrt(A/B) = sqrt(1/2) = 1/sqrt(2) = 70.7%. Max efficiency would occur at 71%.
A useful model to think about, but not exact.
=====================================