DPT conncection size and no. scope

Status
Not open for further replies.

koba78

Petroleum
Joined
May 10, 2011
Messages
30
Location
TW
Dear Sir

The cyclone reactor with DPT and its tube (attached drawing)
I wonder is the process connections should be at least 1/2" NPT and instrument should be equipped with socket or yoke for mounting on a 2" pipe. A yoke is not required if instrument is mounted on a
vessel or process line.
But, the size of this pipe for DPT is decided by instrument or piping ? there is no hint on P&ID. Please help me out.

Thank you very much for your kindly help.
 
Pressure measurments are not normally flowing devices. As such only pressure signals are need. Therefore instrument tubing over piping is generally preferred.

The case for piping connection is defined more for a structural need.

 