Hello mikeangel;
Do you follow North American standards or European standards?
General comments:
Marshalling cabimet:-
Physical characteristics;
The cabinet must be suitable for the location, ie: indoors or outdoors. The codes will specify a type for the intended location.
Size: The cabinet should have adequate working space for the installed terminal strips. Some code may specify minimum clearances to cabinet walls and to adjacent terminal strips.
Company engineering standards may address marshalling cabinet size.
Wiring; preferred method. Use an incoming terminal strip(s) with a terminal for each incoming conductor and an outgoing terminal strip(s) with a terminal for each outgoing wire.
Install interconnecting conductors and jumpers as needed.
Wiring; Economy method, not recommended.
A single terminal strip(s) may be used for both incoming and outgoing conductors with interconnections and jumpers installed on the terminal strip(s).
Transformer:
In North America we would call that a Potential Transformer. It is in the class of instrument transformers that includes Current Transformers. eg: PTs and CTs
The transformer would also be described as having two primary bushings and/or suitable for line to line connection.
Additionally, it would be described as having two secondary windings.
Tell us what code that you work under and someone with specific knowledge will probably help with further suggestions.
Bill
--------------------