Look at thread 403-98883. I asked a similar question on airflows through doors etc and got a lot of useful assistance.
As regards max PD across the door. I don't think there is a recommended value. The PD would be limited by the ability to open the door. You wouldn't want to impede the escapees of a fire. 15 Pa seems a value that can be opened without too much stress.
(Assuming a door for instance 0.8x2m The force on it would be:
F=PxA pressure x area
15N/m2(or Pascals) x 2 x 0.8= 24 Newtons
Convert this to kg Force by F=MA force = mass x acceleration due to gravity (9.81):
Mass = 24N/9.81 = 2.5kG which equates to 5 lB's
I belive that fellow engineers in the Forum have used PD's of up to 25-30Pa without a problem in opening the doors, although I wouldn't like to be doing it on a regular basis.
15Pa is considered adequate in clean rooms for containmant.
In the UK we undercut doors but only when permitted by the nice Building Control Officer. Usually non vision door grilles are fitted with built in fire dampers. Depending on the situation, the dampers can be either intumescent or mechanical. (i.e. if the door is to a plant room, the damper is usually required as intumescent..this is because if the grille is used for fresh air make up, then if a mechanical one closed, there would be no combustion air and a CO problem might occur).
We undercut doors by about 20mm 3/4" so that it maintains fire integrity but gives a reasonable vol flow. I would expect 100l/sec of air through such a gap without any problem.
Again look at the above thread and there are some very useful equations from our colleagues.
Friar Tuck of Sherwood