Question - Is it normal for a Pad-Mount Transformer to have doors blow open when there is an internal arc flash?
Background
+ Equipment = 1.85 MVA transformer at 34.5 KV at a wind farm
+ Initial Electrical Failures - Elbow failure or Bushing failure
+ Typical Fault current 6-20 KA
+ Door Failure - the low-side door only. The high-side door which is bolted down with 2 bolts sometimes bows outward, but has not opened in any of our failures. The low-side door has rods going to the top and bottom and a plate that rotates into a slot when in the closed position.
The manufacturer (a LARGE company) touts that the enclosure has been built and tested to IEEE Std C57.12.28™-2005 (IEEE Standard for Pad-Mounted Equipment—Enclosure Integrity). I've read this standard, and it seems to mainly focus on ensuring the enclosure is built such that it is difficult to break into (penta-bolts, difficult to pry open, etc...) I did not see anything addressing what type of failure the enclosure should withstand. Regardless, I'm sure the IEEE has an opinion on doors flying open and potential hurting people when they do. Is there another standard I should be referencing? All help is greatly appreciated.
Background
+ Equipment = 1.85 MVA transformer at 34.5 KV at a wind farm
+ Initial Electrical Failures - Elbow failure or Bushing failure
+ Typical Fault current 6-20 KA
+ Door Failure - the low-side door only. The high-side door which is bolted down with 2 bolts sometimes bows outward, but has not opened in any of our failures. The low-side door has rods going to the top and bottom and a plate that rotates into a slot when in the closed position.
The manufacturer (a LARGE company) touts that the enclosure has been built and tested to IEEE Std C57.12.28™-2005 (IEEE Standard for Pad-Mounted Equipment—Enclosure Integrity). I've read this standard, and it seems to mainly focus on ensuring the enclosure is built such that it is difficult to break into (penta-bolts, difficult to pry open, etc...) I did not see anything addressing what type of failure the enclosure should withstand. Regardless, I'm sure the IEEE has an opinion on doors flying open and potential hurting people when they do. Is there another standard I should be referencing? All help is greatly appreciated.