Suggestions to navin34 (Electrical) Dec 26, 2003 marked ///\\I would like to know how in an industrial plant the boundary limits for selection of DOL and star delta type of starter are fixed.
///It depends
1. Where you are
2. Voltage level
3. Type of industry
4. Etc.
Sometimes, the limits on DOL are set by standards or practices, e.g. motor max kW may be set to 5kW or max motor HP may be set to 10HP in low voltage power distribution systems. However, some industry, e.g. power generating stations with their fine-tuned auxiliary system may start medium voltage motors DOL as high as thousands of HPs.
The criteria should be set conservatively in an industrial plant. One aspect that has not been addressed yet is a possibility that large motor starts are not mutually exclusive. It means that two or more large motors can start simultaneously. Then, this worst case scenario has to be considered to avoid any trips of upstream protective devices.
The star-delta starters should be compared with modern electronic soft starters since the latter tend to be electrically and mechanically smoother starters.
The DOL limit is set by the motor starting transient voltage at the motor terminal. Depending on the motor design, it can be 85% of the motor terminal (or rated) voltage. The motor can be designed to start DOL with 75% of the motor terminal voltage. It is more expensive. The star-delta starter will reduce the motor starting inrush current approximately to 1/3. This will allow starting the larger HP motor connected to the same power supply.
Visit
(for: Figure 3.3 Current/speed characteristics)
(for: Figure A3.5. Comparison of Current and Torque Reduction With Different Starting Methods.)
etc. for more info.\\ I understand that for deciding this we need to have information about Minimum fault level at MV level and rating of main transformer (MV/LV).
///And mainly, sizes of conductors, i.e. feeders, busways, etc.\\It would be of help if somebody can be little desciptive alongwith the supporting calculations.
///The calculation mainly concentrates on voltage drops across various equipment, e.g.
1. Transformers
2. Cables
3. Overload relays
4. Contacts
5. Power supply internal impedance
6. Etc.
Item Re[volt drop] + jIm[volt drop]
transf
cable
overload
contacts
System Z
etc.
Total = SumRe[volt drop] + jSumIm[volt drop]
Total = |Total| x exp[j atan(sumIm/sumRe)]\\