At the risk of repeating myself, I would like to address the topic of commissioning tests for this forum once again.
In the spirit of full disclosure, I work for a company that builds and provides services with PD diagnostic equipment. ScottyUK is absolutely correct. I am biased but, for very good reasons. Why don’t I work for a company that makes withstand (HIPOT) equipment? There is no future in it. Modern extruded cables do not work like the old paper insulated systems. Please do not compare paper insulated, transformers, motors, cables or any other electrical components with modern extruded components. The failure mechanisms are completely different.
FeinTX,
The Bottom Line:
- DC is no longer supported by IEEE as an acceptance test.
- High potential withstand tests can not assure future reliability.
- A standardize PD test is the test that manufactures have used to prove electrical integrity of extruded components for the last 40 years! Hmmm…. Maybe they are on to something

- A standardized PD acceptance completely eliminates the need for a withstand test. (Basically, if you could get inside a defect while a HIPOT is ‘failing’ it, you would see the material being pitted away and PD all over the place. PD is almost without exception a precursor to extruded system failure)
- No problem with going to 1.5, 2, or even 3x on new systems!! Cables and Accessories are required to withstand routine withstand voltages in excess of 3x the operating voltage for hours. A PD test is only for a few seconds. Again, if you can prove there is no PD and you can be assured that there isn’t an active failure mechanism.
Dandel,
Contractor recommendations:
Yes, many contractors still use a DC HIPOT for commissioning wind farms and would say that it is ‘standard practice’. Unfortunately, what most of them don’t know is that a 110V extension cord will pass a DC HIPOT, yet we all know that it will blow up with medium voltage AC applied. Most contractors who have used a DC HIPOT on extruded cable systems over the last 40 years have developed a false sense of security. This is because nearly all defects will pass the test! What has saved our industry is good design and workmanship practices, not the DC HIPOT. Please help the industry and get the word out. If you want to do a HIPOT, at least do an AC HIPOT. Although the AC HIPOT test can not assure future reliability, at least it creates that conditions that could lead to a failure under test! A low frequency HIPOT (VLF) is the best choice in the destructive, withstand class of tests (IEEE Type 1 test). The caveat with destructive withstand tests is, What if I grow one defect from 10% of in the insulation to 100% and grow another from 5% to 95%?
A true story:
We just did some consulting for one wind farm. They just had a cable failure a few months after the DC HIPOT that took out several turbines. After the wind farm owner lost around $400,000 in revenue and the contractor paid around $80,000 for repairs, what do you think they did, DC HIPOTed the repair and let system go again? I don’t think so. They did a PD diagnostic acceptance test which used the IEEE standards. A proper field PD test repeats the factory PD test on the cable and accessories. They found three other defects on the collector system with the PD test (failures just waiting to happen).
When to use the PD Diagnostic Acceptance Test:
If the world was ideal we would do the same test in the field that the manufacturers use at the factory. However, I know that a standardized PD test isn’t always the right choice for an acceptance test. If you have a URD cable feeding ten customers, so what if it fails? You reconfigure the loop, repair the cable, and move on. However, when you are talking about industrial and commercial plants, one failure can pay for all the PD diagnostics for a whole fleet of plants. Let’s make sure we keep the financial impact in mind when we are making recommendations.
Ask the manufacturer:
I agree with dpc. Check with the manufacture of your joints, terminations, and cable. However, don’t ask them what to do in the field, ask them how they prove the electrical integrity of the components they sell you! That right, if you are talking to a reputable manufacturer they will tell you that every product they sell is 100% tested with a PD test in the factory to IEEE 404, IEEE 48, and ICEA S-94-649 PD specifications. If they are confident with their product they will welcome a PD acceptance test. If the recommend a DC withstand hmm….
IEEE 400-2001 states that if: (once again for this forum)
If the cable system can be tested in the field to show that its partial discharge level is comparable with that obtained in the factory tests on the cable and accessories, it is the most convincing evidence that the cable system is in excellent condition.
An on-line PD test, although it may be useful in some cases, does not fulfill this requirement.
Again, please do not compare paper insulated components with modern extruded components. A few mils of extruded material will withstand a DC test. Ever wonder why you can DC test a cable system without a stress cone at the termination, yet we all know that the cable would fail in service without it? Sure you won’t hurt a new cable with DC but, you won’t find the problems either. So what is the point in going through the exercise of a DC test on an extruded cable system? The only reason I recommend a DC test, if other options are not available, is to assure that someone didn’t leave the other end grounded.
Until next time… take care
Benjamin Lanz
Vice Chair of IEEE 400
Sr. Application Engineer
IMCORP- Power Cable Reliability Consultants