Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Does NFPA 13 address unpackaged bulk storage such as piled grain warehouse? 1

Status
Not open for further replies.

Alireza01

Mechanical
Joined
Feb 14, 2017
Messages
14
Location
IR
Hi
I didn't find any regulation about automatic fire protection system design for unpackaged bulk storage such as piled grain warehouse.
Is it effective to install sprinkler system for such these warehouses?
Is there any criteria for such system design (like NFPA 13)?


 
There are some few references to granular materials in table A.20.4(b) of NFPA 13
 
Alireza01:

FM Global has a loss and prevention sheet on this subject - 7-75.

Link

Regards,

DB
 
Thank you for your replies.
I have some uncertainties about sprinkler system consideration for high roof piled grain warehouses.
1- Since the combustible contents of the warehouse are not integrated solid substances (particulate solid) and possible fire is a surface fire, So I think spraying water is not very effective ( Water is quickly transferred to the bottom of the grain mass)
2- Due to the height of the roof (about 12m), will the heat of the fire cause the sprinkler to activate?
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top