We (testing staff) have had this argument with our network owners for years now, that you must be very careful in interpretation of ddf test results.
It all started (cue wavey lines down screen to indicate step back in time) when we could not get the same results from one day to the next on the same piece of equipment (11kV metalclad switchgear)
After analysis, we performed a large number of controlled tests on epoxy bushings in different temperature and humidity environments.
Because of the small size of capacitance of the epoxy bushings compared to a paper bushing (about an order of magnitude lower) the external effects play a greater part in the measurement circuit. So to get the equivalent ddf reading, your external IR (along the surface) must be much better than that for a paper bushing.
We found that temperature was not a significant factor, however rapid change of temperature could be (ie a step change could possibly form condensation on the surface, but stabilised out over time, the reading was within the expected range for the new temperature.)
The main factor in the differences was humidity, this could change the ddf up to 30X for a change in humidity from 50% to 90%.
Conclusion - if you have a stable environment in your substation (ie airconditioned, positive pressure to keep out dust/dirt etc) DDF could be used as a trending tool, irrespective of the absolute value. If not a stable environment, good luck.
Definitely PD, and even just an inspection of the epoxy can give a good indication as to its quality and the manufacturing quality. We had some gear that had holes from the outer surface through to the conductor. Needless to say that got replaced by the very red faced manufacturer.